Can I connect this hob to the socket ring final via a fused spur, or does it need a bigger supply?
Ta
Ta
Not off of a 2.5mm supply cable its not...
32 amp radial min 4.0mm i dont bother with 4.0 just use 6.0mm
A reasonable rule of thumb is 4 amps per kilowatt, so 3kW is 12A.There's a 6mm cable to the old cooker. Under the hob i'm going to have a 3KW single oven. Can the 6mm feed both?
Or do i need to run another?
A reasonable rule of thumb is 4 amps per kilowatt, so 3kW is 12A.
Apply diversity again and you get 10A + (30% of 2) = 10.6A
Added to the hob you get 10.6 + 14 = 24.6A which is fine with 6mm2, as long as the breaker is appropriately rated.
Please note I don’t do this for a living, but Dunning-Kruger effect aside:Can I have the hob off the 6mm and the oven off the socket ring?......
Ok brill thanks I will do that. Thanks your your help chapsPlease note I don’t do this for a living, but Dunning-Kruger effect aside:
I’d say it’s technically ok to spur a 10.6A load from a ring spur (you have to add 5A if the oven isolator has a socket, mind), but not best practice. You don’t want the oven to suck 1/3 of the ring capacity, nor to take out a load of sockets if it nuisance-trips or needs maintenance.
I’d stick both on the 6mm.